rating of transformer at 2 volt amps

Posted by Doug Criner on 07/10/2009 16:41

Transformers are rated in VA rather than power (W). The temperature rise (and the losses) of a xfmr are related to the load VA rather than the load W.

For example, assume that the load is purely inductive (or capacitive). The power delivered to the load is zero (because the load current and voltage are 90 deg out of phase). But the xfmr may get quite warm, even hot, because: A)the winding is carrying current, giving I^2R losses, and B) the core is continually being magnetized and remagnetized, causing core losses.

But, yes, if you are given load power (W) and, say, the voltage, then to compute xfmr current (A), you need to know the load's power factor.

Now, I forget, what was the question? ;>)
Doug


:::
:::Technically shouldn't the transformers power factor be taken into consideration in figuring the transformer's power using its VA rating?
:::
:::Radiodoc
:::*****************
:::



rating of transformer at 2 volt amps 
Robert 07/03/2009 14:47 
Bob Masse 07/03/2009 15:13 
Doug Criner 07/03/2009 15:22 
Robert 07/03/2009 15:53 
Lewis L 07/03/2009 16:19 
Robert 07/03/2009 16:25 
Lewis L 07/03/2009 17:59 
Doug Criner 07/03/2009 21:11 
Doug Criner 07/03/2009 21:37 
Lewis L 07/04/2009 13:35 
Robert 07/04/2009 20:01 
Doug Criner 07/05/2009 09:38 
Robert 07/05/2009 21:29 
Lewis L 07/05/2009 10:38 
Lewis L 07/05/2009 10:39 
Edd 07/05/2009 13:17 
Doug Criner 07/05/2009 14:52 
Lewis L 07/05/2009 18:58 
Lewis L 07/05/2009 19:58 
Lewis L 07/05/2009 19:58 
Lewis L 07/05/2009 20:01 
Radiodoc 07/09/2009 22:17 
Lewis L 07/10/2009 10:41 
Lewis L 07/10/2009 11:16 
Doug Criner 07/10/2009 16:41 
Radiodoc 07/10/2009 16:46 

   < Previous Message Index Next Message >   




© 1996-2004 Nostalgia Air